Petergg98
Member
- Location
- New Hampshire
- Occupation
- Electrical
I have a cable that needs 200 Amps minimum 105°C (ambient temp is around 180°C). Chart 310.15(B)(1)(2) only lists correction factors up to 66-70°C. What would my next step be?
I don’t understand this sentence. Can you elaborate?I have a cable that needs 200 Amps minimum 105°C (ambient temp is around 180°C).
Is the bold correct?I have a cable that needs 200 Amps minimum 105°C (ambient temp is around 180°C). Chart 310.15(B)(1)(2) only lists correction factors up to 66-70°C. What would my next step be?
I did, sorryDo you mean the ambient is around 180º F ?
No that should be 180°F or 82°CIs the bold correct?
Ampacity is determined by allowable temperature rise. The basic table 310.16 is based on 30C ambient, so the 60C, 75C, and 90C columns are really 30C, 45C, and 60C allowable temperature rise. Then Equation 310.15(B) tells you how to adjust for a lower temperature rise.What would my next step be?
That's true, but the numbers provided in 690.31 should be accurate on the physics of calculating ampacity. So if you have an NEC allowance to use 105C wire in a non-PV application, using the numbers from 690.31 should get you the correct answer.First, you can only use 690.31 if you are using the cable for a PV system.
I don't think that's quite true, it's just pretty uncommon. Looking at 2023 NEC Table 310.4(1) there are several wire types listed with a maximum operating temperature of 150C, 200C, or 250C. They all reference footnote 2 or are limited as "Only for leads within apparatus or within raceways connected to apparatus, or as open wiring (nickel or nickel-coated copper only)"For building power and lighting, you don't have such a thing as 105ºC wire.
This is where I am coming from. The conductor types listed in 31.4(A) and subsequently tables 310.16 through 310.21 are the only conductors allowed for building power and lighting. None of those carry a rating of 105ºC per the NEC, so the OP isn't using 105 wire. Note 3 that you reference is merely telling us that there are only special applications where Z or ZW can be used at 150º. Not an unidentified 105 rated wire.I don't think that's quite true, it's just pretty uncommon.
Cheers, Wayne
I see your point is that Table 310.4(1) doesn't have any allowable insulation types that max out at 105C, entries jump from 90C to 150C. And that it is unlikely that anyone is making wire with an insulation type that could be rated 150C and marking it just 105C. So if the OP wants to go with a higher temperature rating than 90C because the 0.365 temperature correction for 90C wire at 82C is prohibitive for their application, they will end up with a 150C rated wire rather than a 105C rated wire.This is where I am coming from. The conductor types listed in 31.4(A) and subsequently tables 310.16 through 310.21 are the only conductors allowed for building power and lighting. None of those carry a rating of 105ºC per the NEC, so the OP isn't using 105 wire.
Thank you for clarifying NEC idiot tables 310.16 - 310.21, not intended for me, or reasonable people to understand.Note 3 that you reference is merely telling us that there are only special applications where Z or ZW can be used
They really aren't that bad once someone walks you through it. I am pretty sure you can find a video by Mike on the web site to do that. The thing less likely to just "get" is that the wire types are the only wire types you can use unless you were to get some sort of AHJ approval for deviation.Thank you for clarifying NEC idiot tables 310.16 - 310.21, not intended for me, or reasonable people to understand.
Looks like OP may require medium voltage cable with higher-temp ratings, and a transition upsize for the 75C terminations.
You don't have to go to medium voltage to get a temperature rating above 90C.Looks like OP may require medium voltage cable with higher-temp ratings, and a transition upsize for the 75C terminations.