PROBLEM:
20% fill not exceeded but there are over 41 conductors and need to derate per 2008 NEC table 310.15(B)(2)(a).
So, per table 310.16: 90 degree column; THHN #12 AWG Cu has an ampacity of 30 amps.
30A derated at 35% = 10.5A.
On a correction situation, would one prove each branch circuit's load within that ampacity?
OR-
Upsize the conductors?