derating because of conduit fill?

Status
Not open for further replies.

myronelectrician

New member
Location
canton, mi
I have 7 #12 conductors an 5 #10 conductors all thhn in 1 inch emt.
The run is only 20 feet long he says I have to derate the conductors due to conduit overfill, I don't think so according to the conduit fill chart. Is the
Inspector wrong as I suspect? Thanks Guys.
 

jbfan74

Senior Member
Location
Newnan Ga
The inspector is right. Anytime you have more than 3 current carrying conductors in pipe you must derate.
Look at table 310.15(B)(2)(a) to see the percentages.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: derating because of conduit fill?

myronelectrician said:
. . . he says I have to derate the conductors due to conduit overfill. . . .
If you really mean "overfill," which is to say that you put too many conductors in the conduit and exceeded the 40% limit on cross-sectional area, then that is a violation in itself.

However, if you mean that you have more than three current-carrying conductors in the same conduit, then that triggers a requirement for a derating factor.
 