Hi All,
I could not find this previously discussed, so please forgive me if it is a repeat.
I am on the 2011 NEC.
I am looking at a 480V circuit from the basement of bldg going to an equipment shelter located on the roof. Conduits will run vertical through the building to a roof penetration and then across the roof for about 50' until it enters the shelter. Once in the shelter it hits a disconnect switch, then goes into a transformer to give me 208Y/120V.
I am doing ampacity adjustment because the conductors run across the roof. My question is whether or not the code requires the adjustment to continue past the disconnect to the primary lugs on the transformer, OR if I can size the conductors between the disconnect and transformer without adjustment. The length of these conductors may exceed 10', the exception in 310.15(A)(2) doesn't apply.
I would be happy with a code section to answer whether or not the disconnect would be a point whereby I reevaluate for the load side conductors?
I could not find this previously discussed, so please forgive me if it is a repeat.
I am on the 2011 NEC.
I am looking at a 480V circuit from the basement of bldg going to an equipment shelter located on the roof. Conduits will run vertical through the building to a roof penetration and then across the roof for about 50' until it enters the shelter. Once in the shelter it hits a disconnect switch, then goes into a transformer to give me 208Y/120V.
I am doing ampacity adjustment because the conductors run across the roof. My question is whether or not the code requires the adjustment to continue past the disconnect to the primary lugs on the transformer, OR if I can size the conductors between the disconnect and transformer without adjustment. The length of these conductors may exceed 10', the exception in 310.15(A)(2) doesn't apply.
I would be happy with a code section to answer whether or not the disconnect would be a point whereby I reevaluate for the load side conductors?