Bad269
New member
- Location
- Sacramento, CA.
Hello everyone,
I am a first time poster, but have visited the forum when doing research many times. I'd like some opinions on a situation I have with an engineer.
We have a couple trenches that has conduits laying flat on top of each other. Something that I have seen on any job with underground.
The engineer has a detail on the plans calling for spacers for the conduit. Like I have used in the past for utility duct banks, usually 4".
The engineer has stated that if we dont use the spacers he will have to do calculations requiring us to up size conductors. He referred me to N-M calculations. Each conduit has a,b,c phase, neutral and a ground. I have never heard of the need to derate conductors because they asre literally running parallel in a trench. One trench has 4 2-1/2" conduits 2 on bottom 2 on top. the other has 2 2-1/2" conduits on top of 6 1" conduits. Each have the amount of wires I stated before.
I do not see the need for the spacers or derating. He is stating the wires in each conduit are going to heat up adjacent wires in conduits.
Is there a need for derating in this situation?Thank you for any help or info.
I am a first time poster, but have visited the forum when doing research many times. I'd like some opinions on a situation I have with an engineer.
We have a couple trenches that has conduits laying flat on top of each other. Something that I have seen on any job with underground.
The engineer has a detail on the plans calling for spacers for the conduit. Like I have used in the past for utility duct banks, usually 4".
The engineer has stated that if we dont use the spacers he will have to do calculations requiring us to up size conductors. He referred me to N-M calculations. Each conduit has a,b,c phase, neutral and a ground. I have never heard of the need to derate conductors because they asre literally running parallel in a trench. One trench has 4 2-1/2" conduits 2 on bottom 2 on top. the other has 2 2-1/2" conduits on top of 6 1" conduits. Each have the amount of wires I stated before.
I do not see the need for the spacers or derating. He is stating the wires in each conduit are going to heat up adjacent wires in conduits.
Is there a need for derating in this situation?Thank you for any help or info.