I would like to put 12 -#8's and a #10 ground in an 1 1/2 emt. Is this legal cause im not sure how to derate. I know code says 22 #8 thhn in a 1 1/2 emt but Im sure thats not gonna fly in my situation.
Flex said:Does that mean 11 would be the max?
Flex said:I would like to put 12 -#8's and a #10 ground in an 1 1/2 emt. Is this legal cause im not sure how to derate. I know code says 22 #8 thhn in a 1 1/2 emt but Im sure thats not gonna fly in my situation.
Flex said:Im confused on what you mean. would i have to downsize the wire?
Flex said:They are 4, 480v 3phase ckts feeding roof top units.
Flex said:such a huge help man. ive never been taught how to derate, thanks alot
mca is 29.2 ampsiwire said:No problem.
My suggestion is to split it into two raceways, with 6 current carrying conductors in each the derating would only be 80% instead of 50%. Depending in the actual load may get you back in the right.
More important question.
Do you know the name plate data from the units? You should find the MCA (minimum circuit ampacity) and the MOCP (maximum over current protection)
If the MCA is say 27 amps or less and the MOCP is 50 you could use the 8s on the 50 amp breaker.
Flex, Sub-panel Man here. :wink: You might also consider simply running a single set of feeders in that 1-1/2" EMT, and placing a 12-space panel at the point where the circuits would otherwise branch out. It can be more economical and efficient.Flex said:such a huge help man. ive never been taught how to derate, thanks alot
LarryFine said:Flex, Sub-panel Man here. :wink: You might also consider simply running a single set of feeders in that 1-1/2" EMT, and placing a 12-space panel at the point where the circuits would otherwise branch out. It can be more economical and efficient.
.
Then what would be the reason for running them all in the same conduit? :-?iwire said:The RTUs are usually too far apart to make that really pan out.
LarryFine said:Then what would be the reason for running them all in the same conduit? :-?
iwire said:Truth be told we generally run separate cables or raceways to each RTU as per plan.:smile: