The question of derating came up in calculating conductors for a circuit.
If you have for example 7 current carrying conductors in a raceway or cable, the conductors will need to be derated per 310.15(B)(2)(a) at 70%, which we all know. The question was brought up that, if we use 7- #12 THHN 90 degree conductors in a raceway or cable that we can use Table 310.16 allowable ampacity listed in the 90 degree column to start our derating.
I was always taught that per 110.14(C) we need to first start with our temperature terminations due to this being our weakest link in the circuit or system and if we are terminating to 75 degree terminations we need to use the allowable ampacities listed in the 75 degree column to start our derating calculation.
Who's right here???
If you have for example 7 current carrying conductors in a raceway or cable, the conductors will need to be derated per 310.15(B)(2)(a) at 70%, which we all know. The question was brought up that, if we use 7- #12 THHN 90 degree conductors in a raceway or cable that we can use Table 310.16 allowable ampacity listed in the 90 degree column to start our derating.
I was always taught that per 110.14(C) we need to first start with our temperature terminations due to this being our weakest link in the circuit or system and if we are terminating to 75 degree terminations we need to use the allowable ampacities listed in the 75 degree column to start our derating calculation.