Re: derating current-carrying conductors
I would submit that “load diversity” has nothing to do with the total connected load. I would also agree with Dereck’s suggestion that you not try to take advantage of the table you cited, unless you have a calculation sealed and signed by a Licensed PE.
The NEC never defines the term “load diversity,” just as it never defines “volt” or “amp” or a thousand other common terms. Therefore, we are left to presume that it is a common enough term, and that we should apply the “usual definition,” as used in the industry. Unfortunately, the industry has no definition for the term either. The closest standard term, as defined in engineering textbooks, is “Diversity Factor.” It is my belief that “load diversity,” as used in the NEC, is the reciprocal of “Diversity Factor.”
The concept of “Diversity Factor” requires that an overall system be viewed as a collection of smaller subsystems. It looks at the peak load on each of the subsystems, and it looks at the peak load of the system as a whole. It is likely that not all subsystems will hit their individual peak values simultaneously. Therefore, the sum of the individual peak loads will be higher than the system’s overall peak value. “Diversity Factor” is found by dividing the “sum of the individual peak loads” by the “system’s overall peak load.” Note that this means that “Diversity Factor” will most likely be higher than 1, and that it can never be lower than 1. In comparison, “Demand Factor” is always less than or equal to 1.