Elect117
Senior Member
- Location
- California
- Occupation
- Engineer E.E. P.E.
Someone asked me to look over a set of solar plans that has 6 DC circuits (12 total conductors + 1 EGC) per inverter in one conduit. I argued it was 12 CCCs and should be derated as such. They are saying it is 6 CCCs because the negative isn't considered a CCC per NEC 310.15.
Can someone chime in on if the "negative" is considered a CCC (like a neutral in a 120V circuit)?
I think the issue is terminology and I call it a negative and he calls it the grounded conductor. He isn't wrong, but I think that is why I am having a hard time getting him to understand why I think it is 12 CCCs. This code section calls out neutral conductor but does nothing to address grounded conductors.
Can someone chime in on if the "negative" is considered a CCC (like a neutral in a 120V circuit)?
I think the issue is terminology and I call it a negative and he calls it the grounded conductor. He isn't wrong, but I think that is why I am having a hard time getting him to understand why I think it is 12 CCCs. This code section calls out neutral conductor but does nothing to address grounded conductors.