Suppose you have a bank of light switches, say 3... one branch circuit, L & N, enters the box through conduit. Coming out through one conduit, there is one neutral and three travelers -- same wire gauge.
The outgoing conduit would run at the same temperature as, or cooler than, the input. Any time the current is split between travelers the parallel resistance per foot is less and the temperature rise is less.
And yet, for derating purposes, the input has 2 CCC's and is rated 100% but the output has 4 CCC's and is derated to 70%.
This seems silly; is there a way around it?
BTW, my old Book uses the term "diversity" in the derating notes, which are confusing, but "diversity" is not in the index, glossary, or table of contents. It seems to mean that not all wires are energized at once. That wouldn't apply to this case.
The outgoing conduit would run at the same temperature as, or cooler than, the input. Any time the current is split between travelers the parallel resistance per foot is less and the temperature rise is less.
And yet, for derating purposes, the input has 2 CCC's and is rated 100% but the output has 4 CCC's and is derated to 70%.
This seems silly; is there a way around it?
BTW, my old Book uses the term "diversity" in the derating notes, which are confusing, but "diversity" is not in the index, glossary, or table of contents. It seems to mean that not all wires are energized at once. That wouldn't apply to this case.