When Calculating Feeders and Subfeeder conductors, do I apply a 80% continous duty deration factor into my calculation? Or can I just size my conductors to the entire ampacity? What I am getting at is this: I have a 400amp transfer switch, with feeders (500/3 XHHW-2 TC), but if I go to T.310.16, the permitted ampacity is 380, without any deration included. If I apply an 80% Continous Load, (210.19(a), 215.2(a)(1), and 230.42) Ampacity correction factor, that Ampere rating then drops to 304 amps. Which I can only terminate on the Next size higher Breaker at 350 amps, ( 240.4(b)), therefore I am not supposed to terminate 500kcmil xhhw-2 on a 400 amp Breaker, am I correct here? Or is it Legal ?