paulcbrowne
Member
- Location
- Shepherdstown, WV
Article 310, para. 310.15(B)(2)(a) and its table designate limits on the number of current carrying conductors that may be installed in raceway. However, Article 386 describes an exception to Table 310.15(B)(2)(a) for surface metal raceway (SMR) where the cross section is over 4 sq. in. If the fill does not exceed 20%, a maximum of 30 CCCs is permitted.
My question is why would the same not apply if one used 2 1/2 in. EMT whose cross-section is greater than 4 sq. in. (actually 5.858 sq. in.). Both the SMR and EMT can be in a configuration where it is inspectable only at boxes and there is no length limitation for either one. In both, the wires can lie in any random fashion because either SMR like Wiremold or EMT can be installed at any angle.
My question is why would the same not apply if one used 2 1/2 in. EMT whose cross-section is greater than 4 sq. in. (actually 5.858 sq. in.). Both the SMR and EMT can be in a configuration where it is inspectable only at boxes and there is no length limitation for either one. In both, the wires can lie in any random fashion because either SMR like Wiremold or EMT can be installed at any angle.