I am looking at some apartments that have old split bus panels.
They have 4 main breakers at the top. 2@40amp, 1@30 amp, and 1@50 amp serving the lower half of the panel. The lower half is branch ckts only.
I have not kept up with the NEC changes well in the past 10+ years, this is weird, and I need help!
Is it legal now to replace this with a similar panel without upgrading the incoming conductors?
The incoming conductors were either #4 or #6 Aluminum. I could not tell for the age, lack of markings, and they were still hot.
I do not think the incoming service wire size matters either way. I think this cannot be done now, but I have never come across this.
Thank you for your insight.