Does anyone know of any failures due to NOT derating???
I do. I have been failed for not derating twice! Insp was a hard nosed so and so though.
Nice clear concise answer, Charlie.
Does anyone know of any failures due to NOT derating???
The only clarification I am aware of is that the NEC tells us when to count the neutral as a CCC. Absent any other guidance, I would conclude that a conductor is a "current carrying conductor" only when it is capable of carrying current with all associated loads turned on.infinity said:Charlie, although I agree that this is a common sense approach to derating, is it specified anywhere in the NEC that CCC have to being carrying current simultaneously?
The only clarification I am aware of is that the NEC tells us when to count the neutral as a CCC. Absent any other guidance, I would conclude that a conductor is a "current carrying conductor" only when it is capable of carrying current with all associated loads turned on.
JJWalecka said:Here in Massachusetts 310.15(B)(2) is revised ..............
........How is it that Massachusetts is contrary to the NEC?.
JJWalecka said:Iwire,
LOL. I did not know about Table B 310.11 in the back of the NEC.
sandsnow said:Does anyone know of any failures due to NOT derating???
paul said:Don't I get to start in the 90? column when I start my derating for #12 THHN?
dlhoule said:Does anyone know of any failures due to NOT derating???
I do. I have been failed for not derating twice! Insp was a hard nosed so and so though.![]()
![]()
tonyi said:sandsnow said:Does anyone know of any failures due to NOT derating???
I've pulled some pretty toasted ancient #14 out of hot attics where the run probably should have been #12 on a 15A because it was up high near the peak. The same stuff in the walls was less crunchy. It attic stuff hadn't quite failed yet, but it was well on its way.
Good luck with that one. :wink: 8) :lol:JJWalecka said:Now I have to find the definition of Load diversity.
Larry, do you need to prove a failure, or just code violation?sandsnow said:Does anyone know of any failures due to NOT derating???
I was shoping for examples of numerous conductors in a single conduit though.
ramsy said:Larry, do you need to prove a failure, or just code violation?sandsnow said:Does anyone know of any failures due to NOT derating???
I was shoping for examples of numerous conductors in a single conduit though.
Wouldn't Max derating (ie) 12A/25A = 0.39, work for Tbl.310-15(b)2a + 310-16 ambient, or
Max #14's for conduit fill, using 1/2" EMT = 12, from NEC Appendix C.
It's there in 310.15(B)(2)(a), we just can't see it. :lol:infinity said:...only one traveler of the two associated with a three way switch would could as a CCC? IMO only one conductor should count, but I have had asked to back up that opinion with an NEC Article which I can't seem to find.