zinsco
Member
- Location
- San Diego, CA
Installing a 100 amp sub panel that will feed 3-240v 30 amp A/C units only. Main panel is 200 amp.
#1 - Does the sub panel require a neutral even though there will be no loads using a neutral?
#2 - If I do run a neutral, to leave the capability of taking a few 120v loads out, can I derate the neutral and if so to what size?
#3 - Planning on running #2's for my feeder wires, but I was surprised to read somewhere that you could go #4 on the feeder wires for 100 amps to a sub panel. This can't be right. Am I wrong? I would like running #4's if legal.
#1 - Does the sub panel require a neutral even though there will be no loads using a neutral?
#2 - If I do run a neutral, to leave the capability of taking a few 120v loads out, can I derate the neutral and if so to what size?
#3 - Planning on running #2's for my feeder wires, but I was surprised to read somewhere that you could go #4 on the feeder wires for 100 amps to a sub panel. This can't be right. Am I wrong? I would like running #4's if legal.