334.12(B) allows you to sleeve NM for protection against physical damage. So I drop down into a finished garage ceiling (split level house). Instead of putting running boards on the garage ceiling I want to pull (4) 12/2s through a pvc sleeve to get over near the panel. The pvc will not attach to the panel and will have TAs and plastic bushings on the ends.
I have to derate to 70% (8cc conductors). Because NM has 90C conductors do I use the 90C table or (I hope not) start the derate at 60C because that is all NM is good for?
Also, 334.12 B allows a sleeve why is 312.5 C so restrictive when going into a panel (which I am not in this case)? You can only go in the top, can't penetrate a structural ceiling, raceway sealed or plugged at the outer end, minimum raceway 18" max 10' and this is all to avoid having to secure the cable to the Panel. Doesn't make sense to me.
I have to derate to 70% (8cc conductors). Because NM has 90C conductors do I use the 90C table or (I hope not) start the derate at 60C because that is all NM is good for?
Also, 334.12 B allows a sleeve why is 312.5 C so restrictive when going into a panel (which I am not in this case)? You can only go in the top, can't penetrate a structural ceiling, raceway sealed or plugged at the outer end, minimum raceway 18" max 10' and this is all to avoid having to secure the cable to the Panel. Doesn't make sense to me.