howardrichman
Senior Member
If I install 12-12 THHN conductors in 3/4 pvc conduit. According to table 310.15(b)(2)(A), I should be able to install up to 9 conductors- 70% of 30 amps(90c column) to maintain 20 amp rating on those conductors and conduit fill. If I'm interpreting this correctly, Wouldn't the nuetrals be excluded in those calculations and of those 12 conductors. Are the nuetrals and ground current carrying conductors, and counted in the # of conductors? if so would I have to either have to run # 10 conductors for derate, or install another conduit?
please reply;
HR...
please reply;
HR...