I have a store with it's incoming Electrical Service to be 400 Amp/208V/3P. But I don't have the actual demand load, so I assumed the store needs exactly 400AMP.
The drawing calls out for 2 sets (4# 3/0 + 1 #1/0 Ground in 4" Conduit)
Based on Table 310.15(B)(16), 3/0 is good for 200AMP
So 2 Sets of (4# 3/0 + 1 #1/0 Ground in 4"C) is exactly at 400 AMP
If I use Table 310.15(B)(3)(a) for more than Three Current Carrying Conductors, since there are 8 Current Carry Conductors, the percent factor is 70%.
So 2 Sets 2 sets (4# 3/0 + 1 #1/0 Ground) with a 70% factor is only good for 280AMP
But when I use Cerrowire Ampacity Calculator, (default temp), they said it's good for 315A.
So based on Cerrowire Ampacity Calculator, I would need to use at least 250kcmil, which would come out to 406A.
My calculation came out as 250kcmil at 255 AMP. So (2*255*.8) = 357 AMP
How do I fix my canulation so I can get similar answers to the calculator.
Do I need to include the neutral and ground for my calculation for deratings and Conduit Size.
Based on Conduit Fill Calculator, I believe I can fit about 17 conductors for 3/0 or about 11 Conductors for 4" for 250kcmil in a 4" Conduit.
So instead of running 2 separate 4" Conduit, can I ran everything in 1 4" Conduit.
I believe based on the calculation, will a 2 Sets of 4#250kcmil+1#1/0G in a 4" Conduit work for 400AMP
The drawing calls out for 2 sets (4# 3/0 + 1 #1/0 Ground in 4" Conduit)
Based on Table 310.15(B)(16), 3/0 is good for 200AMP
So 2 Sets of (4# 3/0 + 1 #1/0 Ground in 4"C) is exactly at 400 AMP
If I use Table 310.15(B)(3)(a) for more than Three Current Carrying Conductors, since there are 8 Current Carry Conductors, the percent factor is 70%.
So 2 Sets 2 sets (4# 3/0 + 1 #1/0 Ground) with a 70% factor is only good for 280AMP
But when I use Cerrowire Ampacity Calculator, (default temp), they said it's good for 315A.
So based on Cerrowire Ampacity Calculator, I would need to use at least 250kcmil, which would come out to 406A.
My calculation came out as 250kcmil at 255 AMP. So (2*255*.8) = 357 AMP
How do I fix my canulation so I can get similar answers to the calculator.
Do I need to include the neutral and ground for my calculation for deratings and Conduit Size.
Based on Conduit Fill Calculator, I believe I can fit about 17 conductors for 3/0 or about 11 Conductors for 4" for 250kcmil in a 4" Conduit.
So instead of running 2 separate 4" Conduit, can I ran everything in 1 4" Conduit.
I believe based on the calculation, will a 2 Sets of 4#250kcmil+1#1/0G in a 4" Conduit work for 400AMP