derating/parallel conductors

Status
Not open for further replies.

jemsvcs

Senior Member
For a 400A service with all service entrance conductors paralled and in the same stick of RMC, and taking into account derating according to Table 310.15(B)(2)(a), Table 310.16 shows using at least 350 kcmil cables. With 6 total cables in the the RMC, it should be 3 to 3.5" based on Table C9.

So, why do I see so many paralleled 4/0 conductors in 3" RMC for a 400A service?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: derating/parallel conductors

Originally posted by jemsvcs:
So, why do I see so many paralleled 4/0 conductors in 3" RMC for a 400A service?
Most people will be using 4/0 90 C conductors but they are also in a wet location which means in most cases they will need to be figured at 75 C.

4/0 @ 75 C is rated 230 amps * 2 runs * .8 adjustment factor resulting in an ampacity of 368 amps.

This is fine for a 400 amp service if the calculated load is under 368 amps.

See 240.4(B) and 240.6

[ September 07, 2005, 04:40 PM: Message edited by: iwire ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: derating/parallel conductors

For what it is worth any 400 amp service I have built used one set of 600 Kcmil CU or two sets of 4/0s in separate raceways minimum.

[ September 07, 2005, 04:49 PM: Message edited by: iwire ]
 

pierre

Senior Member
Re: derating/parallel conductors

For what it is worth, the Residential Building
Code permits paralleled sets of 4/0 for 400 amp services in single or separate raceways - Table E3503.1

In NYS, this supercedes the NEC
 

badjeepr

Member
Re: derating/parallel conductors

4/0 @ 75 C is rated 230 amps * 2 runs * .8 adjustment factor resulting in an ampacity of 368 amps.
Cant the 90 degree column always be used for derating conductors?
 

jemsvcs

Senior Member
Re: derating/parallel conductors

Earlier I meant to reference Table C8 in reference to RMC.

The way I see it is this:

1. Table 310.15(B)(6) allows 4/0 Al for a 200A Service.
2. 4/0 Al @ 75C is only rated for 180A.
3. Taking into account the derating factor, 300 kcmil Al @ 75C would give us 230 x 0.8 = 184A per conductor.
4. So two paralleled 300 kcmil conductors should be permissible - and 3" RMC would also be acceptable.

Any comments on the reasoning here?

Thanks,

Jemsvcs
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: derating/parallel conductors

Cant the 90 degree column always be used for derating conductors?
Only if the conductors are rated for 90?C. If you are using THHN/THHW it is only rated for 75?C in wet locations and you start with the 75?C rating for the derating. Note if the wire type has a "-2" suffix, it can be used at the 90?C rating in both wet or dry locations.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: derating/parallel conductors

Jemsvcs, 310.15(B)(6) and Table 310.15(B)(6) are specific in text and there is no allowance to parallel any conductors using the tables derated ampacities.

Although, I guess if you were to utilize 310.15(C) (pay an engineer) you could do it. ;)

Roger
 

jemsvcs

Senior Member
Re: derating/parallel conductors

Roger,

If i'm going to pay those kind of rates to get the same answer I might as well send my lawyer some money too. :roll:

Jemsvcs
 