4 # 1/0 to 150 amp circuit breaker using 90 degree wire 1/0 rateing is 170 amps.
if i derate 80% the rating is now 136 amps. to small a rating for 150 amp,
does this sound right.
i think i should use 2/0 90 degree at 195 amps x 80% is 156 amps.
any comments.
135 amps yes on the neutral
If the calculated load is 135 and the conductor ampacity is 136, the code permits the use of a 150 amp OCPD to protect the conductor.135 amps yes on the neutral
ok what if this is from the secondary side of a 45kva transformer.
no next size up rule there.
ok what if this is from the secondary side of a 45kva transformer.
no next size up rule there.
Looks to me like you'd be fine with the next size up OCPD based on 240.4(B) and 450.4.
450.4 is for "Autotransformers" :?
SO THE WIRE SIZE SHOULD BE 2/0 correct
I think 3/0. Not sure.http://ecmweb.com/content/transformer-installation-made-easysort
Oops once again.:ashamed1:Der?k, the OP is showing a 150A ocpd on the secondary, not a 175 as shown in your illustration.
ok if i were ocpd at 175 .
but at 150 ocpd it should be 2/0
We don't know that yet, because you have not told us what type of load is being served. The grounded conductor would be counted as a current carrying conductor only if the major portion of the load is non-linear.so the 4 conductors have to be derated
lets say it does it feeds a panel that feed outlets