I was looking at an installation the other day, rather then change the main service panel, the electrician ran a 2" sealtight from the main service to a larger load center. He removed the feeder going into the house from the main breaker and ran it to the new panel. From the new load center he ran a feeder back (through the same raceway) to the main panel and spliced it to the original feeder. There are now six 2/0 cu. in the 2" sealtight, 4 current carrying conductors. this is a 200 amp service and they used table 310.15(B)(6) to use 2/0cu instead of 3/0cu. So my question is, since there are now 4 CCC's in the same conduit and it requires derating to 80% based on 310.15(B)(2)(a), would you start to derate from 200 amps or 175 amps? I say 175 amp, This means a jump to 250MCM. Now the 2" sealtight is too small. :blink: