Have several 3P 30A motor circuits. They have 3 #10 hots, 1 #10N and 1 #10G.
If I were to combine two of these circuits in one pipe I would be limited to 70% of the ampacity listed in the 90 degree column?
So using THHN @ 90 degrees #8 is good for 55A. I would have to take 70% of that which is about 38A. So I could use #8's? Thanks