Do I have to derate the service entrance conductors that are in PVC conduit from the utility transformer to the service located in the building when I have 4 conductors in each conduit of a parallel run (total of 8 conduits)?
Another estimator here is saying the adjustment factors do NOT apply based on Art. 310.15(B)(3)(a)(3).
Does anyone know the intent of this article? Does this article even apply (we are entering the building and the article states entering or leaving an outdoor trench)?
In this case derating the conductors will actually make a difference in the job.
Please send me your interpretation of this.
Thanks,
Jon Sathre
Another estimator here is saying the adjustment factors do NOT apply based on Art. 310.15(B)(3)(a)(3).
Does anyone know the intent of this article? Does this article even apply (we are entering the building and the article states entering or leaving an outdoor trench)?
In this case derating the conductors will actually make a difference in the job.
Please send me your interpretation of this.
Thanks,
Jon Sathre