dana1028
Senior Member
- Location
- San Francisco Bay area
Got into a discussion with someone -
In T310.16 'Correction Factors' - you would adjust a THHN conductor using a correction factor of 1.04 when you had an ambient temperature of 70F....then apply any other derating factors for conduit fill, etc.
However, it was argued, since there is no correction factor given for temperatures below 70F, then you would not [could not] arbitrarily use a correction factor of 1.04 for an ambient temperature of 68F; thus, you would make no adjustments.
It was argued that if the 1.04 correction factor was valid for temps below 70F then the table would so indicate.
I argued that the correction factor of 1.04 was valid for an ambient temp of 68F. That said, I don't know what you would use for very cold ambients.
Could someone provide some insight? Is there a code section?
In T310.16 'Correction Factors' - you would adjust a THHN conductor using a correction factor of 1.04 when you had an ambient temperature of 70F....then apply any other derating factors for conduit fill, etc.
However, it was argued, since there is no correction factor given for temperatures below 70F, then you would not [could not] arbitrarily use a correction factor of 1.04 for an ambient temperature of 68F; thus, you would make no adjustments.
It was argued that if the 1.04 correction factor was valid for temps below 70F then the table would so indicate.
I argued that the correction factor of 1.04 was valid for an ambient temp of 68F. That said, I don't know what you would use for very cold ambients.
Could someone provide some insight? Is there a code section?