Presuming you want to know what minimum size of "equipment grounding conductor" is needed, as mentioned table 250.122.
Also keep in mind if you are using metal raceway, the raceway itself does qualify as an equipment grounding conductor, but if you still decide to pull a "wire type" EGC it still needs sized by 250.122.
The grounded (neutral) conductor in this feeder can be sized to the actual maximum unbalanced load connected to it, but also can not be smaller then the values in table 250.122 - so if you had a calculated neutral load of 30 amps you still would need a 6 AWG minimum neutral conductor on a 200 amp feeder.