I told my boss today that you can put 7-9 #12 AWG current carrying conductors into a 3/4" pipe each protected by a 20amp breaker.
I used table 310.15(b)(16) and 310.15(C)(1) to calculate that 7-9 #12s in a conduit can be rated at 21amps.
My boss claims that I can't use the 90 degree column to do my calculation because the circuit breaker terminal is only rated for 70 degrees.
Can anyone shed some insight on this disagreement?