Hi,
I am giving a class on 2005 code revisions and wish to use an example of the effect of derating.
This is an actual installation this facility is getting ready to install.
Twelve 120-volt 20-amp branch circuits to feed individual duplex receptacles to charge utility vehicles.
(I am assuming they are linear loads, subject to change based on manufacturer?s response.)
(Four multiwire circuits from a 120/208 3-phase panel.)
The existing plan is to run the conduit along the roof conduit rack in direct sunlight.
I wish to show the effect of the new FPN 310.10.
A typical summer day here is 98F. That gives an ambient of 128F using the new FPN.
(20 amp rating of branch circuit) divided by (0.76 for a 128F temp factor) divided by (50% for 12 current carrying conductors) equals 52.63 rounds up to 53 amps, which requires number 8 wire.
(Good for 40 amps at 60F)
(Is it correct to round 0.5 and higher up and round below 0.5 down on final derating value?)
If instead they stay inside the building and run along the wall in two separate conduits then:
(20 amp rating of branch circuit) divided by (1.0 for 86F temp factor) divided by (80% for 6 current carrying conductors equals 25 amps, which requires a number 14 wire. (Good for 20 amps at 60F)
However 240.4(D) will require #12 wire.
Is this correct or have I missed something.
Thanks for your help,
Andy
[ July 05, 2005, 06:33 PM: Message edited by: andy32821 ]
I am giving a class on 2005 code revisions and wish to use an example of the effect of derating.
This is an actual installation this facility is getting ready to install.
Twelve 120-volt 20-amp branch circuits to feed individual duplex receptacles to charge utility vehicles.
(I am assuming they are linear loads, subject to change based on manufacturer?s response.)
(Four multiwire circuits from a 120/208 3-phase panel.)
The existing plan is to run the conduit along the roof conduit rack in direct sunlight.
I wish to show the effect of the new FPN 310.10.
A typical summer day here is 98F. That gives an ambient of 128F using the new FPN.
(20 amp rating of branch circuit) divided by (0.76 for a 128F temp factor) divided by (50% for 12 current carrying conductors) equals 52.63 rounds up to 53 amps, which requires number 8 wire.
(Good for 40 amps at 60F)
(Is it correct to round 0.5 and higher up and round below 0.5 down on final derating value?)
If instead they stay inside the building and run along the wall in two separate conduits then:
(20 amp rating of branch circuit) divided by (1.0 for 86F temp factor) divided by (80% for 6 current carrying conductors equals 25 amps, which requires a number 14 wire. (Good for 20 amps at 60F)
However 240.4(D) will require #12 wire.
Is this correct or have I missed something.
Thanks for your help,
Andy
[ July 05, 2005, 06:33 PM: Message edited by: andy32821 ]