If I run a number of wires in a single conduit. and have to derate the allowable ampacity to 40 percent .. then what size breakes is used ??
There are 12 motors, all have name plate 21 amps .. they are 3phase . that gives 36 wires in the conduit .. and if single each circuit would be wired with #10s and on a 30 amp breaker. now I run the circuits all in one conduit, that reduces the allowable ampacity , 40% , so I upsize the wire to bring it back up over my 21 amps for each motor, if the wire size is now #8 and my allowable ampacity is 21 amps , what size breaker is needed .. 30 amp?
or is the breaker sized top the reduced ampacity of the gang of wires ..
some one else advised that ... these 36 #8 conductors in a single conduit would only be 22 amps and not adequate for a 30 amp feed. #6 conductors would be correct for a 30 amp requirement.
what is right ??
There are 12 motors, all have name plate 21 amps .. they are 3phase . that gives 36 wires in the conduit .. and if single each circuit would be wired with #10s and on a 30 amp breaker. now I run the circuits all in one conduit, that reduces the allowable ampacity , 40% , so I upsize the wire to bring it back up over my 21 amps for each motor, if the wire size is now #8 and my allowable ampacity is 21 amps , what size breaker is needed .. 30 amp?