I have a customer that wants to supply three 3-phase heater loads, each fused at 30amps.
He wants to install one conduit that is about 100FT to a junction box and then split off to each heat bank.
We must first derate the wire by (0.7).
#8 is good for 50amps x 0.7 = 35amps.
1. Is it okay to carry one #8 EGC (good for 100amps) and jump it to each heat bank?
2. Does the ground get derated as well?
3. Minimum Conduit Size for 10-#8 THHN? I am guessing 2".
My code book is 20 miles away.
I will confirm when I get back to the office. Any help would be appreciated.
  
[ October 19, 2004, 10:03 AM: Message edited by: dcsva@aol.com ]
	
		
			
		
		
	
				
			He wants to install one conduit that is about 100FT to a junction box and then split off to each heat bank.
We must first derate the wire by (0.7).
#8 is good for 50amps x 0.7 = 35amps.
1. Is it okay to carry one #8 EGC (good for 100amps) and jump it to each heat bank?
2. Does the ground get derated as well?
3. Minimum Conduit Size for 10-#8 THHN? I am guessing 2".
My code book is 20 miles away.
I will confirm when I get back to the office. Any help would be appreciated.
[ October 19, 2004, 10:03 AM: Message edited by: dcsva@aol.com ]
 
				