bennny123
- cudahy,California
How do we know when u have to derate or do temp correction factor.
Welcome to the forum. Derating, or "adjustment factors", is covered in 310.15(B)(2)(a) for # of CCC in a raceway, and in the following pages for high (>30*C/86*F) ambient temperatures. There are numerous exceptions, such as sleeves/nipples <24", traveler legs or conductors that cannot be simultaneously energized, etc.
So if its only 3 ccc won't need to use adjustment factor do we then just do the math on the number they gave us..
Same thing with a ambient temp ? If doesn't pass 86*F
Yes, you would do the math based on the full ampacity of the wiring (at 90*C). Keep in mind you're still limited by 240.4(D) on small conductors.
You have to derate (use a smaller breaker) when the adjustment factors limit the wiring to less current than the OCPD is rated for. 9 #12s (all CCC) in a conduit would be .7 x 30A = 21A, still fine for a 20A breaker. 9 #10s (all CCC) tho give .7 x 40 = 28A, so a 30A breaker wont work there.
Would the next standard size up rule possibly apply?