Derating
simplyme
My local church runs a camp that recently had a gym built on site. The father in law of one of the members did the wiring of the gym lights. He ran a 3/4 emt conduit, with seven circuits running to the lights. Each circuit fed no more than 4 400w, 120v lights. He used #12 THHN to feed the lights. Figuring the de rating on those wires in the conduit, we start at 30a, derate 70% to bring us to 21a, he placed each circuit on a 20a breaker. Now figuring the draw on the lights, each light draws 3.4a, with no more than 4 lights on a circuit, we are less than 14a total load. The inspector failed it, saying that he should have began his de rating calculation a 20a instead of 30a. When my friend approached me with this, I can't find any fault with the installation, is the inspector correct and I'm missing something? Any input is appreciated. I brought this problem to another electrician friend and he opened a whole other can of worms, saying he thinks the de rating should be down to 50% because you count the neutrals, I don't do a ton of de rating calcs, but I've never counted the neuts and never had a problem...Thanks in advance for any replies.
Re: Derating
The inspector is wrong and your friend may be right. You haven't given quite enough information.
Is this a 120Y/208v or a 277Y/480v system, or is it a single phase system and how many neutrals are in the conduit?
See 310.15(B)(2)(a)
Roger
[ May 27, 2005, 09:36 PM: Message edited by: roger ]
Re: Derating
Roger, thanks so much for the reply, my de rating has always been done on single phase. And the gym is a single phase service. But the neutrals would be counted on 277/480 as the neuts carry an imbalance, am I right? BTW, beautiful state, your North Carolina. We visit the Charlotte area often, as we have friends there. We have thought about moving there ourselves from time to time.
Re: Derating
Simplyme,
you are kind of right. Actually this is true in the pure definition of "Neutral Conductor" in single or three phase systems.
Where a problem occures is when only two phases of a three phase system is used with a neutral the neutral will carry pretty much the same current as the other conductors.
Being that you have a single phase system I am going to assume (That can be dangerous ;) ) you have L1-N-L2, L1-N-L2, L1-N-L2, and L-N, this will give you 8 current carrying conductors which will equate to a 70% derating of the conductors so your 21 amp number is correct.
Thank you, it is a nice place to live.
Roger
Re: Derating
Assuming that the lighting is incandescent and that the installer has balanced the load, and used a common neutral for every two circuits; there will be 8 currren-carrying conductors which puts you in the 70 percent adjustment factor.The derating factor is applied to the ampacity of the conductor. No. 12awg has an ampacity of 30A, therefore, .70 x 30A = 21A. The size of the overcurrent device cannot be any greater than 20A. The inspector is incorrect.
Re: Derating
and the reason he is incorrect is because you start with the ampacity of the conductor in the 90 deg column not the 60 deg column for derating puposes.