mstrlucky74
Senior Member
- Location
- NJ
If running lighting circuits from panel and you have a (6) 20a circuits with separate neutrals then you have 12 current carrying conductors and must derate by 50%. #10’s are good for 35A at 75 degree but if running all 6 circuits in one pipe from 20A breakers you could not use #10’s as they would only be good for ~17A, correct?