So looking to run 1-1/4” EMT with seven 1P 20A circuits that have separate neutrals and one ground. This would be #10 THHN wire fed from 20A breakers and would be feeding receptacles.
That would be 15 wires and would need to derate 50% according to 310.15B and bring the #10 wire good for only 17.5. IS that correct or could I use the 90 degree column when derating?