Yes I'm on a roll today. Sorry.
Had a thought, and I think a good one...uh oh.
Have the two circuits below from that panel about 120' away. Both pieces of equipment are right next to each other.
Thinking I have two options but not sure if the combined homerun one makes sense.
1. Run each of the circuits in a separate conduit from panel to equipment.
2. Run a common pipe with both circuits to a box right above the equipment then peel off to both. Since there would be 8 CCC's I would need to derate(70%) so I would have to run #8's then I can splice in the box above the equipment to #10's.
Any reason option #2 would be less practical then #1??