O.K. folks..help me out here...after many years of inspecting I kinda know the Code, but someone asked a question which, I feel, involves more engineering than Code. The Notes to the ampacity tables give a adjustment factor for more than 3 current carrying conductors in
a raceway. Lets assume I have a 420 amp 3 phase load(non cont). I can feed that with a 600 MCM Cu.(420 amp) If on the other hand, I decide to feed with parallel conductors in ONE conduit, due to derating, I can't use 4/0's (260x2x.8). Yet the 4/0 is rated at 230, and from one point of view (2) 4/0s = (1) 600. Both situations produce approximately the same % conduit fill.
Why do we still need to derate if we a paralleling conductors?
a raceway. Lets assume I have a 420 amp 3 phase load(non cont). I can feed that with a 600 MCM Cu.(420 amp) If on the other hand, I decide to feed with parallel conductors in ONE conduit, due to derating, I can't use 4/0's (260x2x.8). Yet the 4/0 is rated at 230, and from one point of view (2) 4/0s = (1) 600. Both situations produce approximately the same % conduit fill.
Why do we still need to derate if we a paralleling conductors?