Is it me or has the way you derate changed in the code from 2005 to 2008?
I was looking at NEC 2005 vs. NEC 2008 handbook for derating examples. I did not find a calculation in 2005, but what I found online on ecmweb.com gave examples of multiplying the derating factor. However, in 2008 handbook there is a calculation example (page 310-311) that divides the derating value making the amps of the wire more, thus possibly resulting in a bigger wire (pipe) size. Has anyone reviewed this? If you have, what is your take on how to calculate this?
Also, its my understanding that the code states for devices rated over 800A the conductors shall be equal to or greater than the rating of the OCPD. So if you have a 2000A device and you derate per 2005 (multiply) would you have to upsize your wire to meet 240.4C?
I was looking at NEC 2005 vs. NEC 2008 handbook for derating examples. I did not find a calculation in 2005, but what I found online on ecmweb.com gave examples of multiplying the derating factor. However, in 2008 handbook there is a calculation example (page 310-311) that divides the derating value making the amps of the wire more, thus possibly resulting in a bigger wire (pipe) size. Has anyone reviewed this? If you have, what is your take on how to calculate this?