Derating

Status
Not open for further replies.

bennie

Esteemed Member
According to the NEC under what conditions is it a requirement to connect a No.#10cu to a 20 amp breaker?

[ July 07, 2003, 10:53 PM: Message edited by: bennie ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Derating

There are no code sections that require a #10 conductor be conencted to a 20 amp overcurrent protective device. There are code sections that require that, under some conditions, the maximum OCPD for a #10 to be 20 amps or less.
Don
 