B bennie Esteemed Member Jul 7, 2003 #1 According to the NEC under what conditions is it a requirement to connect a No.#10cu to a 20 amp breaker? [ July 07, 2003, 10:53 PM: Message edited by: bennie ]
According to the NEC under what conditions is it a requirement to connect a No.#10cu to a 20 amp breaker? [ July 07, 2003, 10:53 PM: Message edited by: bennie ]
P pierre Senior Member Location Westchester County, New York Jul 8, 2003 #2 Re: Derating Bennie When thats all you have left in the truck. When the helper brings you 10 awg (before color coding) instead of 12 awg. When the AHJ tells you to. Pierre
Re: Derating Bennie When thats all you have left in the truck. When the helper brings you 10 awg (before color coding) instead of 12 awg. When the AHJ tells you to. Pierre
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jul 8, 2003 #3 Re: Derating There are no code sections that require a #10 conductor be conencted to a 20 amp overcurrent protective device. There are code sections that require that, under some conditions, the maximum OCPD for a #10 to be 20 amps or less. Don
Re: Derating There are no code sections that require a #10 conductor be conencted to a 20 amp overcurrent protective device. There are code sections that require that, under some conditions, the maximum OCPD for a #10 to be 20 amps or less. Don