Hi All,
I used to work at a company that would do dual-services to a critical facility with two utility switchgear (A & B) and generator paralleling switchgear (A & B) to provide standby power. To avoid the cost of a modified differential ground fault system (MDGF), they'd only provide a 3-wire system but the utility would only provide a wye-connected transformer secondary. Based on my understanding of the NEC, section 250.24(C) requires you to bring the neutral into your service disconnect. This is probably a stupid question but do you just bond the neutral to the ground bus in the switchgear and keep it from being distributed throughout your system and therefore it's technically a 3-wire system? How else would you do it? Based on my understanding / experience, delta-connected secondaries are not really used anymore since they'd be corner-grounded and you'd have a wild-leg phase which can be problematic if you aren't meticulously labeling equipment.
Any feedback would be greatly appreciated. Thank you.
I used to work at a company that would do dual-services to a critical facility with two utility switchgear (A & B) and generator paralleling switchgear (A & B) to provide standby power. To avoid the cost of a modified differential ground fault system (MDGF), they'd only provide a 3-wire system but the utility would only provide a wye-connected transformer secondary. Based on my understanding of the NEC, section 250.24(C) requires you to bring the neutral into your service disconnect. This is probably a stupid question but do you just bond the neutral to the ground bus in the switchgear and keep it from being distributed throughout your system and therefore it's technically a 3-wire system? How else would you do it? Based on my understanding / experience, delta-connected secondaries are not really used anymore since they'd be corner-grounded and you'd have a wild-leg phase which can be problematic if you aren't meticulously labeling equipment.
Any feedback would be greatly appreciated. Thank you.