I've hooked up a few transformers but usually just like the specs say. Also, either there is a neutral already there or I don't need one.
I see a post sometimes mentioning deriving a neutral where there is none.
Could someone explain to me how that's done?
Please do it so my simple mind can comprehend it!:blink:
if the secondary winding isn't tapped for a neutral, well, going in with
a piece of aluminum bus and a tig welder may affect the ul listing a bit.
you need a place to land X0 somewhere, and unless you are doing something
like building two or three separate single phase xfmr's into an array, there
isn't any way to do it that i'm aware of. there are only two places that neutral
can be attached to the secondary winding... where all the windings connect in
a wye secondary, and the centertap of the A-C winding in a delta.
sometimes i've had to run a xfmr backwards to get 480 for a load in a 208
or 240 volt occupancy, but i've never needed a neutral for something like that.
i dimly remember the zigzag thing from apprenticeship. that's the last time i've
seen one.... right in there with quadrophonic stereo systems.
a three phase delta secondary is supposed to have one phase grounded.
the first time you do it, it feels kinda odd tying B phase to ground, and turning it on.