I'm an engineer foraying into article 517 for the first time. Working on a dermatology clinic being fit out into a strip mall shell space. Tell me if I'm missing something:
1. 517 applies to a dermatology clinic per 517.1 Scope and 517.2 definition of a Health Care Facility.
2. Provide effective ground-fault current path per 517.13(A). Can be conduit or flex as allowed by 250.118. (I saw something in another post about "hospital-grade MC cable" - what is that, and does it apply here?)
3. 517.13(B) requires an insulated equipment grounding conductor be pulled to each receptacle, metal box, and the surface of fixed electrical equipment blah blah blah.
4. 517.14 Panelboard Bonding. I don't think we have "normal" and "essential" branch-circuit panels so do not believe this applies. I basically will pull one or two 208V/3P/200A panels off the spare meter sockets. No generator, no UPS. So as long as I run the grounding conductors to the ground bar within each panel, and then connect each of the ground bars back to the service ground, I'm good - right?
5. 517.17 Ground-fault Protection does not apply - no life-support equipment (plus the service entrance is 120V to phase, so no ground fault breaker to coordinate with).
6. 517.18(A) Patient Bed Location - does not apply to clinic per exception #2. Also there are no "patient beds" as defined in 517.2.
7. 517.18(B) Patient Bed Location Receptacles - again, there are no "patient beds" as defined in 517.2, so this does not apply.
8. 517.18(C) Pediatric Locations - anyone care to guess what (if anything) is considered a pediatric location in a dermatology clinic? I do not believe "pediatric" is defined in the NEC. I will run this one by the Owner, I have a feeling they will know the answer.
9. 517.19 - Critical Care Areas - I do not believe this applies. Anyone have any reason to believe a small (four exam rooms, two procedure rooms) pediatric clinic would have critical care areas? I will also run this one by the Owner as I believe the "general/critical" distinction ultimately comes from them.
10. Part III, Essential Electrical System. This applies per 517.25 Scope. I am assuming this just means emergency lighting - this is where the article gets a little harder to follow. 517.30-35 is for hospitals, 517.40-44 is for nursing homes...so that leaves 517.45(A) and (D), which don't say much. I assume I should have battery emergency lights in the corridors, exam rooms, procedure rooms, lobby, etc. I assume no UPS or generator is required.
11517.60 Anesthetizing locations - I assume none of this applies, but will send a few questions into the Owner regarding anesthesia.
Eh, crap, I still have a number of sections to go through (low-voltage equipment, diagnostic equipment, therapeutic equipment, guarding and grounding, communications & fire alarm and isolated power systems) but need to get out of the office. I'll check in tomorrow and see how far off track you all say I am. FWIW my boss has a little experience in this, but isn't available the early part of this week as I'm trying to get it off the ground - but will have someone in-house looking over my shoulder. Thanks in advance!
1. 517 applies to a dermatology clinic per 517.1 Scope and 517.2 definition of a Health Care Facility.
2. Provide effective ground-fault current path per 517.13(A). Can be conduit or flex as allowed by 250.118. (I saw something in another post about "hospital-grade MC cable" - what is that, and does it apply here?)
3. 517.13(B) requires an insulated equipment grounding conductor be pulled to each receptacle, metal box, and the surface of fixed electrical equipment blah blah blah.
4. 517.14 Panelboard Bonding. I don't think we have "normal" and "essential" branch-circuit panels so do not believe this applies. I basically will pull one or two 208V/3P/200A panels off the spare meter sockets. No generator, no UPS. So as long as I run the grounding conductors to the ground bar within each panel, and then connect each of the ground bars back to the service ground, I'm good - right?
5. 517.17 Ground-fault Protection does not apply - no life-support equipment (plus the service entrance is 120V to phase, so no ground fault breaker to coordinate with).
6. 517.18(A) Patient Bed Location - does not apply to clinic per exception #2. Also there are no "patient beds" as defined in 517.2.
7. 517.18(B) Patient Bed Location Receptacles - again, there are no "patient beds" as defined in 517.2, so this does not apply.
8. 517.18(C) Pediatric Locations - anyone care to guess what (if anything) is considered a pediatric location in a dermatology clinic? I do not believe "pediatric" is defined in the NEC. I will run this one by the Owner, I have a feeling they will know the answer.
9. 517.19 - Critical Care Areas - I do not believe this applies. Anyone have any reason to believe a small (four exam rooms, two procedure rooms) pediatric clinic would have critical care areas? I will also run this one by the Owner as I believe the "general/critical" distinction ultimately comes from them.
10. Part III, Essential Electrical System. This applies per 517.25 Scope. I am assuming this just means emergency lighting - this is where the article gets a little harder to follow. 517.30-35 is for hospitals, 517.40-44 is for nursing homes...so that leaves 517.45(A) and (D), which don't say much. I assume I should have battery emergency lights in the corridors, exam rooms, procedure rooms, lobby, etc. I assume no UPS or generator is required.
11517.60 Anesthetizing locations - I assume none of this applies, but will send a few questions into the Owner regarding anesthesia.
Eh, crap, I still have a number of sections to go through (low-voltage equipment, diagnostic equipment, therapeutic equipment, guarding and grounding, communications & fire alarm and isolated power systems) but need to get out of the office. I'll check in tomorrow and see how far off track you all say I am. FWIW my boss has a little experience in this, but isn't available the early part of this week as I'm trying to get it off the ground - but will have someone in-house looking over my shoulder. Thanks in advance!