aceonskis

Member
Location
Midland Texas
Occupation
Electrician
Just finished a masters test and ran across a question about design B motor conductor size. The HP was given 10 and it was 3phase 208. Im not sure where to start with this, i don't see it in the FLC tables. Anyone seen this before?
 
"Design B" is a red herring, it doesn't matter, probably thrown in there to mess you up. It's just a 10HP 208V motor as far as conductor sizing is concerned.
 
Thank you for replying first of all.
Ok well that's good i thought there might be something special about it. the conductors offered in the question stated at #6 and went up from there, this motor should have an FLC of 30.8 so i assume you multiply by 1.25 but that still doesn't get you to #6. Thoughts?
 
NEMA design A, B, C, D essentially determines what amount of inductance is used in the stator vs the rotor. In a Steinmetz circuit it is X1 and X2. It determines the shape of the torque curve and starting current but has no effect on FLC.
 
Thank you for replying first of all.
Ok well that's good i thought there might be something special about it. the conductors offered in the question stated at #6 and went up from there, this motor should have an FLC of 30.8 so i assume you multiply by 1.25 but that still doesn't get you to #6. Thoughts?
“Should have” is irrelevant. You size the conductors based on the FLC listed for your HP and voltage in the appropriate chart in the NEC, section 430, x 1.25. It doesn’t matter if the actual FLC is lower, but it does of it is higher (like on a 12 pole motor or something unusual), in which case you use the higher value.
 
Thank you for replying first of all.
Ok well that's good i thought there might be something special about it. the conductors offered in the question stated at #6 and went up from there, this motor should have an FLC of 30.8 so i assume you multiply by 1.25 but that still doesn't get you to #6. Thoughts?
I question whether they had the right answer if 6 AWG was the smallest conductor in the possible answers. Table 430.250 says 10 HP 208 volt three phase motor is 30.8 A like you said. times 1.25 = 38.5. 8 AWG is minimum copper conductor, even if only 60C insulation.

Unless there were other reasons to make more adjustments that you neglected to read or tell us about.
 
Did it say single or three phase? Single would be about 55 amps.

Can you post the full question?
Thanks for the reply
“Should have” is irrelevant. You size the conductors based on the FLC listed for your HP and voltage in the appropriate chart in the NEC, section 430, x 1.25. It doesn’t matter if the actual FLC is lower, but it does of it is higher (like on a 12 pole motor or something unusual), in which case you use the higher value.
Thank you Jraef
I feel the same way about it. I only missed passing by 2 questions so I wanted to know as much as I could about, that question comes up every time it seems.
 
I question whether they had the right answer if 6 AWG was the smallest conductor in the possible answers. Table 430.250 says 10 HP 208 volt three phase motor is 30.8 A like you said. times 1.25 = 38.5. 8 AWG is minimum copper conductor, even if only 60C insulation.

Unless there were other reasons to make more adjustments that you neglected to read or tell us about.
Thanks Kwired
I came up with the same answer myself. The question was so vague. No other info. That’s why I thought that the design B maybe had some special note that I haven’t ran across and I have all the new 2020 mike holt stuff and I can’t find anything. I appreciate you time helping me with this.
 
Thanks Kwired
I came up with the same answer myself. The question was so vague. No other info. That’s why I thought that the design B maybe had some special note that I haven’t ran across and I have all the new 2020 mike holt stuff and I can’t find anything. I appreciate you time helping me with this.
I'd ask them their answer and how they come up with it. Maybe let us know what they said. With no more information than given, I don't see why 8 AWG wouldn't be the correct answer though.
 
I'd ask them their answer and how they come up with it. Maybe let us know what they said. With no more information than given, I don't see why 8 AWG wouldn't be the correct answer though.
Yeah, #6 might be correct if there was along distance and you had to deal with voltage drop, or you are running conductors for 3 motors in one conduit and had to de-rate, or it is aluminum wire, some other mitigating circumstance. But if what you posted was the entirety of the data you had to work with, they are not correct.
 
Yeah, #6 might be correct if there was along distance and you had to deal with voltage drop, or you are running conductors for 3 motors in one conduit and had to de-rate, or it is aluminum wire, some other mitigating circumstance. But if what you posted was the entirety of the data you had to work with, they are not correct.

Technically, #6 is not incorrect. Nothing prohibits running oversized conductors as long as it’s done properly.

I know, I’m reaching here
 
Technically, #6 is not incorrect. Nothing prohibits running oversized conductors as long as it’s done properly.

I know, I’m reaching here
Kind of have to assume the question was asking what is minimum size conductor allowable for the situation, if they don't state that then anything larger is also a valid answer.
 