Another inspector posed this question to me in regard to Art 225 ('08)
225.33 allows the disconnecting means for a detached building to consist of no more than six circuit breakers.
225.38(B) calls for the "simultaneous disconnect of all ungrounded supply conductors"
Does this mean if one uses the six circuit rule that you would need a listed handle-tie for the up to six breakers ?
A second question deals with 225.39. (D) which requires the disconnect means have a rating of not less than 60 amps.
If one has a 100 amp MLO panel with (3) 20 amp s.p. breakers on a 240/120 supply does that meet the 60 amp requirement ?