Looking at a house with a 100 amp feed to a main lug panel in a detached garage.
4-wire feed to the panel from the house
6 Spaces, 6 breakers in use
Unbonded
No EGC in place (easy fix)
Panel was installed maybe 15-20 years ago based on what I think is a date code.
Aside from local inspectors who might have said ok based on a misinterpretation with there being 6-throws, was this ever allowed (or not explicitly prohibited)?
Seems like one of those 'probably ok but not compliant' situations if I assume it was actually inspected at installation.
Opinions appreciated.
Dave