Hi All - I'm a project manager and electrical engineer with more experience doing odd-ball power distribution and control stuff for science / defense industry. Oftentimes, the work is exempt from the NEC. We do our calculations and build accordingly. Every now and then I find myself paging through the NEC, either to inform a design choice that is not strictly dictated by the NEC or to double check compliance on a project that will have to be inspected. But residential / commercial wiring is not my bread and butter. Electricians know it way better than I do, which is why I'm here!
I've got a side project that will need to be inspected and I want to make sure I do it right from the beginning. Currently, I have a building with a 200 amp service with a 30 amp sub-panel in a detached building. The detached building is about 720 square feet and will be home to a small R&D machine shop. The 30 amp sub-panel needs to be replaced with a 200 amp service. The first thing I'm planning is to replace the 200 amp pan on the first building with a 320/400 amp pan with dual lugs. Here's where things get a little tricky...
Due to the location of the overhead drop, along with trees, pavement and some underground tanks, the shortest, easiest route to the second building is basically through the first building, which is prohibited (I believe) by article 230.3, presumably because there is no over-current protection on the feeder. So I'm trying to come up with a legal solution. Here's what I've got:
From 320A pan, run SER to first building's 200 amp MB panel. In parallel, run another length of SER to a 200 amp fused disconnect, located in close proximity to the first building's MB. From the 200 amp fused disconnect, run RHW through the first building and then underground (18" deep direct burial with ribbon at 12") to the second building. Since the second building is not connected to the first building in anyway, I would not run a ground wire - only split phases and neutral. The second building would then get two 10' ground rods with 6' separation. I've got the testing equipment to check ground resistance on those; there's quite a bit of ledge around here so getting a good ground rod in can sometimes be tough.
Does this sound kosher? The two things I'm particularly concerned about:
1) Two service disconnects in one building - Again, article 230 explicitly forbids a building from having more than 1 service, with a few exceptions. Does a disconnect that feeds a detached building count as a service? It's just a disconnect, no spaces where a midnight electrician might be tempted to plug in breakers and start feeding the first building.
2) Grounding - I still get confused with grounding requirements for detached building. Since this is detached from the first building with no water mains, gas pipes, etc. joining the two, I think it gets its own ground, which would then be bonded to the neutral at the panel. But... I've got a service disconnect inside the first building. Does that mean I have to run a ground from the 2nd building's ground system to the disconnect? Do I have to bond the neutral there and not at the breaker box? Then sizing the ground wire and where to place the rods? Ugh!
Or is this one of those cases where I just bite the bullet and go with a really long run of USE from the pan to the second building and be done with it? The cost of excavation and material will be significantly higher, though...
Thanks!
I've got a side project that will need to be inspected and I want to make sure I do it right from the beginning. Currently, I have a building with a 200 amp service with a 30 amp sub-panel in a detached building. The detached building is about 720 square feet and will be home to a small R&D machine shop. The 30 amp sub-panel needs to be replaced with a 200 amp service. The first thing I'm planning is to replace the 200 amp pan on the first building with a 320/400 amp pan with dual lugs. Here's where things get a little tricky...
Due to the location of the overhead drop, along with trees, pavement and some underground tanks, the shortest, easiest route to the second building is basically through the first building, which is prohibited (I believe) by article 230.3, presumably because there is no over-current protection on the feeder. So I'm trying to come up with a legal solution. Here's what I've got:
From 320A pan, run SER to first building's 200 amp MB panel. In parallel, run another length of SER to a 200 amp fused disconnect, located in close proximity to the first building's MB. From the 200 amp fused disconnect, run RHW through the first building and then underground (18" deep direct burial with ribbon at 12") to the second building. Since the second building is not connected to the first building in anyway, I would not run a ground wire - only split phases and neutral. The second building would then get two 10' ground rods with 6' separation. I've got the testing equipment to check ground resistance on those; there's quite a bit of ledge around here so getting a good ground rod in can sometimes be tough.
Does this sound kosher? The two things I'm particularly concerned about:
1) Two service disconnects in one building - Again, article 230 explicitly forbids a building from having more than 1 service, with a few exceptions. Does a disconnect that feeds a detached building count as a service? It's just a disconnect, no spaces where a midnight electrician might be tempted to plug in breakers and start feeding the first building.
2) Grounding - I still get confused with grounding requirements for detached building. Since this is detached from the first building with no water mains, gas pipes, etc. joining the two, I think it gets its own ground, which would then be bonded to the neutral at the panel. But... I've got a service disconnect inside the first building. Does that mean I have to run a ground from the 2nd building's ground system to the disconnect? Do I have to bond the neutral there and not at the breaker box? Then sizing the ground wire and where to place the rods? Ugh!
Or is this one of those cases where I just bite the bullet and go with a really long run of USE from the pan to the second building and be done with it? The cost of excavation and material will be significantly higher, though...
Thanks!