Detached building
nizak
Would a 6 space MLO panel in a detached garage fed from a house require a main disconnect?
Thank you.
Assuming that the panel in the detached garage is located nearest the point of entry of the feeder conductors into the garage, the MLO panel is fine even if there is space for more than six breakers. As long as only six are installed it is code compliant.
Thank you.
. . . the MLO panel is fine even if there is space for more than six breakers. As long as only six are installed it is code compliant.
My less-than-perfect memory tells me differently. I vaguely recall that you would have to somehow permanently disable any breaker positions beyond the allowable six. My code book is not handy, so Charlie's Rule will not help me today. Any comments?
While many inspectors enforce that way, there is nothing in the code rule that says that.
225.33(A) General.
The disconnecting means for each supply permitted by 225.30 shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or switchgear. There shall be no more than six disconnects per supply grouped in any one location.
I see nothing that even suggests that the panel not be able to accept more than 6 breakers.
Thanks, Don. I remember seeing it somewhere, but that somewhere might not have had any official status.
Most MLO breaker panel labels I have seen have language like: Suitable for Service Entrance when not more than 6 protective devices are installed.
The label does not cover every conceivable handle configuration, but it clearly expresses the intent to meet 225.33.
Yes, but the requirement that the second building disconnect to be listed as suitable for use as service equipment was last seen in the 2011 code.
There is no restriction on the number of spaces in the panel, only on the number of disconnects that are installed at the time of inspection.
Absolutely correct.
The label wording I saw seems to be common on many if not most MLO panels. So I put 2 and 2 together to get apples instead of oranges.🙁
Absolutely correct.
Yes, and service rated disconnects were required prior to the 2008 code when you could just run the ungrounded conductors and grounded conductor to the second building as the neutral was bonded at the second building just like at a service. Requiring that the disconnect be listed as use as service equipment resulted in a factory supplied means of neutral bonding.
The requirement for SUSE for the second building should have been deleted in the 2008, but it tool a couple of cycles before that happened.