Our customer's detached garage had an electrical fire that started in the attic space and he wants to know if there were any obvious violations. The garage was built with the house in 1995. The garage is supplied by a 3 wire, 100A feeder inside the main switch panel in the main house on 1awg aluminum to an MLO panel in the garage. The feeder has NO ground wire run with the 2 hots and neutral and the N and G bars and not bonded inside the garage subpanel.
Violations:
1 - I know this was built under some 1990s code but the first violation that I'm guessing was code even back then is, being a separate building supplied by a feeder, there is no disconnect mean at the building. The feeder attaches directly to the MLO subpanel with not separate disco. It has more than 6 breakers btw so the 2-6 rule is not valid.
2 - I understand prior to 2008, 250.32.B.2 allowed the option to run the feeder w/o an EGC and use the grounded N conductor as the ground fault path back to the main panel. However, doesn't this require N and G to be bonded in the subpanel? Otherwise, how would a ground fault, let's say up in the attic space, make its way from the branch circuit EGC to the grounded N to clear the fault? In fact, all of the branch circuit ground wires terminate on the subs grounding terminal strip and, other than being connected to the building grounding system (GEC), they go nowhere after that. So they basically do nothing as far as EGC.
3 - The feeder conduit also has 2 branch circuits leaving the subpanel going back down the conduit, one to the gate motor and the other is unlabeled. I see no issue with feeders and branch cons in the same conduit but we couldn't find any junction box above ground where they would separate out those branch circuits. So is it buried under the concrete, or worse?
Any input agreeing or disagreeing or if more info is needed to determine this accurately would be helpful. I hate being that guy that calls out previous work without having all my facts straight.
Violations:
1 - I know this was built under some 1990s code but the first violation that I'm guessing was code even back then is, being a separate building supplied by a feeder, there is no disconnect mean at the building. The feeder attaches directly to the MLO subpanel with not separate disco. It has more than 6 breakers btw so the 2-6 rule is not valid.
2 - I understand prior to 2008, 250.32.B.2 allowed the option to run the feeder w/o an EGC and use the grounded N conductor as the ground fault path back to the main panel. However, doesn't this require N and G to be bonded in the subpanel? Otherwise, how would a ground fault, let's say up in the attic space, make its way from the branch circuit EGC to the grounded N to clear the fault? In fact, all of the branch circuit ground wires terminate on the subs grounding terminal strip and, other than being connected to the building grounding system (GEC), they go nowhere after that. So they basically do nothing as far as EGC.
3 - The feeder conduit also has 2 branch circuits leaving the subpanel going back down the conduit, one to the gate motor and the other is unlabeled. I see no issue with feeders and branch cons in the same conduit but we couldn't find any junction box above ground where they would separate out those branch circuits. So is it buried under the concrete, or worse?
Any input agreeing or disagreeing or if more info is needed to determine this accurately would be helpful. I hate being that guy that calls out previous work without having all my facts straight.