I'm looking for wire/cable suggestions for a 100 amp feeder to a detached garage. It's only a forty foot run. Normally I use individual conductors in raceway but wanted to look at some other options, this is my first residential job. Looks like USE and UF may be alternatives as well as Tray Cable. Which leads me to my next question.
The panel label states "Line Terminals A,B, and N Suitable for 60/75 C Conductors". The breakers state "CU-AL 60/75 C Wire". One code class I went to the instructor said the 60/75 meant you could use the 75 deg ampacity for motors (100 amps or less). I've also read on here a circuit breaker 60/75 C rating means if the breaker is installed alone in an enclosure you can use the 75 deg C ampacity but if it's in a load center with other breakers you have to use the 60 deg C.
So my question is even if the incoming line terminals are 60/75 the branch breakers in the panel would only be good for 60C, because they are next to each other, so the wire supplying the panel would have to be rated 60 deg C?
I see that the type UF (TC) may be limited to 60 deg C anyway. (NEC 2020 - 340.80) Is that right?
Additional information:
The supply side of this feeder will splice to an existing 4/0-4/0-4/0 & 2/0G, AL, SE style R that runs through the attic, down the inside of a wall and ends in a box on an exterior wall.
The homeowner has also stated they prefer the wire or cable be installed in conduit.
Thanks for any input.
The panel label states "Line Terminals A,B, and N Suitable for 60/75 C Conductors". The breakers state "CU-AL 60/75 C Wire". One code class I went to the instructor said the 60/75 meant you could use the 75 deg ampacity for motors (100 amps or less). I've also read on here a circuit breaker 60/75 C rating means if the breaker is installed alone in an enclosure you can use the 75 deg C ampacity but if it's in a load center with other breakers you have to use the 60 deg C.
So my question is even if the incoming line terminals are 60/75 the branch breakers in the panel would only be good for 60C, because they are next to each other, so the wire supplying the panel would have to be rated 60 deg C?
I see that the type UF (TC) may be limited to 60 deg C anyway. (NEC 2020 - 340.80) Is that right?
Additional information:
The supply side of this feeder will splice to an existing 4/0-4/0-4/0 & 2/0G, AL, SE style R that runs through the attic, down the inside of a wall and ends in a box on an exterior wall.
The homeowner has also stated they prefer the wire or cable be installed in conduit.
Thanks for any input.