goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I'm planning on running a 50 amp 120/240 feeder in PVC ( 3 # 6's and 1 # 8) to a detached garage and installing a main lug panel w/ a max capability of 6 circuits (BTW, garage is literally detached by about 18"). The total run is less than 50' and the main service was upgraded two years ago. Inspector tells me that I need (2) ground rods to re-establish the ground at the sub panel.
A) Do I need 2 ground rods ? The way I read 250.32 I only need one.
B) Do I need a main disconnect in the garage or does the 6 switch rule apply ?
Tnx.
A) Do I need 2 ground rods ? The way I read 250.32 I only need one.
B) Do I need a main disconnect in the garage or does the 6 switch rule apply ?
Tnx.