Hello,
looking to clear up some confusion with the code that I have. When wiring a detached garage and running a 3-wire 20-amp branch circuit to it, the requirements for circuits are to my understanding.
210.52(G) lists detached garages for the receptacle, Dedicated.
210.70(A)(2)(a) lists detached garages for an inside light
210.11(C)(4) Garage Branch Circuits
210.70(A)(2)(b) lists detached garages for an outside man door light
230.79(B) 2 circuit instillation 30-amp disconnecting means
I can run 2 20-amp circuits with a 30-amp disconnecting double pole switch at the point of entry into the garage. One circuit is for dedicated 20-amp rec. and the other can be used for lighting and GDO. Just making sure I'm not missing anything? The customer just wants the bare minimum on his rental property, to resupply power to the garage.
looking to clear up some confusion with the code that I have. When wiring a detached garage and running a 3-wire 20-amp branch circuit to it, the requirements for circuits are to my understanding.
210.52(G) lists detached garages for the receptacle, Dedicated.
210.70(A)(2)(a) lists detached garages for an inside light
210.11(C)(4) Garage Branch Circuits
210.70(A)(2)(b) lists detached garages for an outside man door light
230.79(B) 2 circuit instillation 30-amp disconnecting means
I can run 2 20-amp circuits with a 30-amp disconnecting double pole switch at the point of entry into the garage. One circuit is for dedicated 20-amp rec. and the other can be used for lighting and GDO. Just making sure I'm not missing anything? The customer just wants the bare minimum on his rental property, to resupply power to the garage.